Ash26

-
Joined
Nov 12, 2011
Messages
14
Reaction score
1
Hi there - I’m changing the CU in my two bed terraced for my ELECSA assessment and just want to make sure that I’ve got everything right.

Existing:pME, 60A service head, 16mm tails to meter and 16mm to 60A BS88 isolator/switchfuse, 8metre 16mm T&E sub-main to 30 yr old Wylex 60A. Main earth is via the T&E, 10mm bonding to gas/water. Ze at CU is 0.41.

Calculated maximum loading to be about 45A

Plan to upgrade to Wylex 9 way split load, (due to width restriction of 300mm) with 100A main switch, 1x80A 30mA RCD with 4 MCB and 2xRCBO’s, main earth to 16mm, change T&E to 16mm XLPE SWA (for additional protection, and future capacity).

Using 16mm SWA restricts capacity to 89A (Note 1 on table 4E4A refers to 512.1.5, so used 4D4A ref method C), so do I need to change 100A main switch in the CU and the isolator/switch fuse to 80A and get DNO to upgrade meter tails and main cut out ?

Many thanks for your help.....
 
Last edited:
How are you disconnecting supply while you carry out CU change? My advice is to find out if the DNO will fit you a DP isolator for free (EON do). That way, you can isolate and do the job at your convenience rather than have the fuse pulled by the DNO in the morning and reconnected in the afternoon.
If your service fuse is 60A then your in-line 60A isolator/switchfuse is fine.
 
16mm is fine on a 60A fuse. Ze looks high though, for TNC-S. should be under 0.35.

He should try taking the Ze from the supply side of the switch fuse, close to the service cut-out. That T&E earth could be the problem, along with any loose connections in the earthing system...

Id say 16mm tails are good for up to a 80A service fuse.
 
Thanks Telectrix and Engineer54 - I'll take a reading from the supply side of the switch fuse. It looks like 10mm earth from the service head to the switch fuse.....
 
Thanks Telectrix and Engineer54 - I'll take a reading from the supply side of the switch fuse. It looks like 10mm earth from the service head to the switch fuse.....

Better still take the earth measurement from the PME connection block on the cut-out, using the fuse switch for your line connections. May also be prudent to check the tightness of any earth connections at the cut-out PME terminal block. You can then start checking connections back to the CU if improvement is found!!

You may also be on a supply cable that's in the process of being PME'd, in which case you can well have a slightly higher Ze value. This will then be more of a TNC-S supply rather than a full PME supply!!! lol!!!
 
He should try taking the Ze from the supply side of the switch fuse, close to the service cut-out. That T&E earth could be the problem, along with any loose connections in the earthing system...

Id say 16mm tails are good for up to a 80A service fuse.
Yep eng....Ze being the external ......so as close as to the origin of supply (DNO cutout)......
 
Couldn't see how to get to the earth connection at the cut-out PME block to check, but gave it a tug and appeared ok.....But Ze is 0.39 there....
 
Last edited:

Reply to CU change and sub main upgrade in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
771

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
483
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top