Hi all this is my first post so sorry if i ramble on a bit!!
My problem is that i have changed an old cu with a dual rcd 17th cu. when the upstairs ring is on one of the rcds and the downstairs ring is on the other and i plug any appliance in it trips the downstairs ring. i have changed the rcd, did IR test on downstairs ring these all worked/appeared fine , but still problem occurs. I have moved all circuits on to one rcd and that seems to solve problem,
any ideas? thanks in advance .dan
 
Sounds like a neutral problem for sure. Are you 100% that you had both legs of the same ring connected together on the same RCD, not one leg of one ring and one of the other?

Also, double check the split load kit in the CU, maybe an issue there somewhere.
 
dan that sounds like a crossed neutral ,like the others have said a circuit will run fine if you have a crossed or borrowed neutral untill you add a load ,on shared neutrals between ground and 1st floor say when you have 2 rcds and a lighting circuit on each with shared neutrals ,IE neutral to landing light being borrowed from an unstaire light ,if its that this would normally trip both RCD's
 
have checked both legs of both rings and they are in the correct bars . will go back tomorrow with a clear head and check on all the suggestions made thank you all for help..:)
 

Reply to CU Change problems in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
123
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
910
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...
Replies
4
Views
493
A fully charged car battery should have a resting voltage of 12.6 volts
Replies
4
Views
374

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top