Hi Guys,
Just been to quote a job for a CU change, not a problem but I noticed some cable cores were silver (all red & black sleeve), the rest copper R&B sleeve. I assume this is aluminium but I have never seen this before, I know it could probably do with a rewire but if I change the CU only at this moment in time, does that conform as long as it tests OK?
Cheers
 
hi

Alu conductors were about years ago, they became more popular because of copper shortages in the 70's. So you come accross them now and again.
They are much more brittle than copper and its really down to an assessment of their state, including insulation and subject to test.

I'd also check that they are of the correct size, you usually find that they are a size higher than copper, e.g 4.0mm used instead of 2.5mm for ring main. This is due to alu having a higher resisitivity than copper. So check they are suitable.

They should be ok but due to their age the insulation may have broken down a bit and also become dodgy, and if stranded cored the ends may become brittle so i'd avoid moving them about more than neccessary.

From a peridoc inspection point of view, you may wish to assess that under an observation and recommendation - depending on their state - that they may require improvement under a 2 classification.
 
Only you can know by looking, but entirely possible they`re actually tinned copper - in which case they`d still be candidates for rewiring but may still comply if testing proved sound. However, look carefully, as if they are tinned copper they may well be imperial sized which generally means a smaller CSA. Some circumspection called for then.
 
Hi Guys,
Just been to quote a job for a CU change, not a problem but I noticed some cable cores were silver (all red & black sleeve), the rest copper R&B sleeve. I assume this is aluminium but I have never seen this before, I know it could probably do with a rewire but if I change the CU only at this moment in time, does that conform as long as it tests OK?
Cheers


Are you sure they are not stranded tinned copper as early twin and earth was. The larger sizes were due to them being imperial sizes

2.5mm was 7/0.029
1mm was 1/0.044
 
Thanks for your replys guys.
Been back today and taken a closer look, they are stranded tin plated wires, did some testing and with the exception of low IR tests showing around 50Mohms all seems ok. Continuity and Zs was ok.
 

Reply to CU Change in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
897

Similar threads

  • Question
There is no homework, and I'll never see these photo again.
Replies
3
Views
608
Definitely looks like the cpc (earth) has been sleeved and used as a neutral conductor, this is not permitted. You are going to need an...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top