Is this allowed, its's not in any zones.... above door at 2600mm and far aenough away from bath not to get sprayed.

Another CU change to do and not sure whether it's got to be moved / never come across one in bathroom before :confused:
 
From the OSG

Accessories allowed and SELV sockets-outlets and shaver supply units to BS EN 61558-2-5 allowed. Socket-outlets allowed 3m horizontally from the boundry of zone 1

Although as Chapter 701.411.3.3 Adittional protection shall be provided for all circuitsof the location

So you incoming supply would have to be RCD protected before entering the bathroom
 