Can a (eg, MK BS4293 63A 30mA) RCD be used as a main switch in a CU if it's the ONLY source of switching for that CU? I'm about to start work on a CU with RCD-Breaker-Breaker-Breaker-etc-Main Switch-Breaker-Breaker-Breaker-etc.

I obviously need to add a new RCD for the second split but would the board then need a main switch for the whole thing? These boards used to have labels saying something like "All switches must be off to disconnect from the supply".

...wondering...
 
All installations should have a single point of isolation. One RCD switching the second can be done but you need to have some discrimination (possibly a time delay RCD).

As you are undoubtedly aware the partially compliant 17th edition boards have a main switch that feed both RCD's.

A cheap way out would be to have a DP 100A switch in a 2 way enclosure and use it to feed both RCD's? Mark it up as main switch and everyone is happy !
 
All installations should have a single point of isolation. One RCD switching the second can be done but you need to have some discrimination (possibly a time delay RCD).

As you are undoubtedly aware the partially compliant 17th edition boards have a main switch that feed both RCD's.

A cheap way out would be to have a DP 100A switch in a 2 way enclosure and use it to feed both RCD's? Mark it up as main switch and everyone is happy !

Thanks Phil....there is a 100A Hager 2-pole switch on the tails so we're hunky-dory there. I've not had the covers off the CUs (there are 2) so I'll need to check if they share any common bars inside. The board here is undoubtedly 16th Edition.....I need to take a peek inside tomorrow.
 
Last edited:

Reply to CU - RCDs as the main switch? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
897

Similar threads

  • Question
those old mk rcds are very fast the figure you have quoted is the maximum allowed not the typical times,I have seen mk ones trip at 9 ms , the...
Replies
5
Views
1K
  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
829

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top