All
I have just completed a CU upgrade. I wont talk about the borrwoed neutral between the up and down lights!!! However, the lighting circuits, although in pvc do not have a cpc. I have advised the customer and given him a price to re-wire the lights, which he says will accept but is not in the positio to proceed at this stage. There fore I have been unable to measure the R2 and Earth loop impedance on the lighting circuits (cos there aint one!!) Any way I am in the process of completing the EIC and will clearly document the fact that there is no earth present for the lighting circuits and this is a limitation. Can some one advise if there is gonna be any come back with inspection body if this is inspected before the lights get re-wired?
Thx in advance.
Lurch
I have just completed a CU upgrade. I wont talk about the borrwoed neutral between the up and down lights!!! However, the lighting circuits, although in pvc do not have a cpc. I have advised the customer and given him a price to re-wire the lights, which he says will accept but is not in the positio to proceed at this stage. There fore I have been unable to measure the R2 and Earth loop impedance on the lighting circuits (cos there aint one!!) Any way I am in the process of completing the EIC and will clearly document the fact that there is no earth present for the lighting circuits and this is a limitation. Can some one advise if there is gonna be any come back with inspection body if this is inspected before the lights get re-wired?
Thx in advance.
Lurch