I'm trying to challenge myself with scenarios where I'm not sure if my interpretation of the calculation rules + regs is correct or not.
RFCs are doing my head in.
I think I understand most of the theory:
- 433.1.204 lists a specific case where a RFC protected by a 30/32A protective device may be employed. In there, it says, "Such circuits are deemed to meet the requirements of 433.1.1 if the current carrying capacity (Iz) of the cable is not less than 20A..." (and some other stuff about high single point loads).
So that seems pretty clear - when determining the appropriate cable size (taking into account all the rating factors and the reference method), It should be 20A or more.
Without any rating factors, then for either singles (70C thermoplastic insulated, table 4D1A) or T&E (table 4D5), 2.5mm is ok for most common rating factors listed in the tables, apart from 101 (It=17A) and 103 (It=13.5A). For instance, reference method A (enclosed in conduit in an insulated wall) is 20A.
My confusion relates to grouping factor. If you run the two legs of the RFC in separate conduit, then you're ok. But if you run the two legs of the ring in the same conduit, does that mean you need to apply Cg=0.80 (table 4C1)... in which case 2.5mm cable will no longer be adequate?
I wondered if note 9 below that table would help; but in the worst case scenario, where 20A is in one leg, and 12A in the other, then 12 is greater than 0.3x20, so can't be discounted.
Even reference method B ("enclosed in conduit on a wall") would not be suitable; It=24A and 0.8x24 = 19.2A, which is less than the stated miniumum Iz of 20A.
So, do we simplify all that to: "Don't run your two legs of your RFC down the same conduit, as it won't meet the CCC, and 433.1.204"?
Or is there another take on this?
I'm trying to challenge myself with scenarios where I'm not sure if my interpretation of the calculation rules + regs is correct or not.
RFCs are doing my head in.
I think I understand most of the theory:
- 433.1.204 lists a specific case where a RFC protected by a 30/32A protective device may be employed. In there, it says, "Such circuits are deemed to meet the requirements of 433.1.1 if the current carrying capacity (Iz) of the cable is not less than 20A..." (and some other stuff about high single point loads).
So that seems pretty clear - when determining the appropriate cable size (taking into account all the rating factors and the reference method), It should be 20A or more.
Without any rating factors, then for either singles (70C thermoplastic insulated, table 4D1A) or T&E (table 4D5), 2.5mm is ok for most common rating factors listed in the tables, apart from 101 (It=17A) and 103 (It=13.5A). For instance, reference method A (enclosed in conduit in an insulated wall) is 20A.
My confusion relates to grouping factor. If you run the two legs of the RFC in separate conduit, then you're ok. But if you run the two legs of the ring in the same conduit, does that mean you need to apply Cg=0.80 (table 4C1)... in which case 2.5mm cable will no longer be adequate?
I wondered if note 9 below that table would help; but in the worst case scenario, where 20A is in one leg, and 12A in the other, then 12 is greater than 0.3x20, so can't be discounted.
Even reference method B ("enclosed in conduit on a wall") would not be suitable; It=24A and 0.8x24 = 19.2A, which is less than the stated miniumum Iz of 20A.
So, do we simplify all that to: "Don't run your two legs of your RFC down the same conduit, as it won't meet the CCC, and 433.1.204"?
Or is there another take on this?