Morning
The company that I work for has recently had an electrical inspection carried out. One of the findings consisted of 'ineffective overcurrent protection of cable due to rating of protective device and CSA of cable'
Basically a 100A isolator was feeding a 16mm SWA. The SWA conforms to BS 5467 and according to Table 4E4A a 16mm Ref. Method E can carry 99A.
Would it be prudent to downgrade the isolator to 63/80A or for the sake of 1A would the 100A Isolator suffice?
In addition numbers quoted in ERA report 69-30 Part V allows 107A for a 16mm SWA.
Thank you for your help
Cameron.