Just wondering if anyone has anyone information on this:
Been asked to quote on a rewire for a 1 bed flat. The cutout and prepayment meter is in the shop below. (1 cut-out - henley blocked into 2 supplies) The flat and shop are owned by different people - but the shop owner allows the folks from upstairs to come into his shop, go behind the counter and top up their electricity. Understandably, the owner of the flat wants this changing, as he doesn't think that the shop owners are always going to want his tenants doing this. Is this set-up even permitted? Given that the flat tenants can't access the main fuse (or their own meter) anytime the shop is closed?
Further more, the sub-main supply up to the flat is via an old switch fuse, into a 10mm T&E.
They have 9.5kw shower, Ceramic Hob and an immersion heater!
To start with, I'm thinking of advising the sub-main be changed to 16mm SWA from switch fuse, with separate 10mm earth - any thoughts on this? (total run is 5m)
Many thanks
Been asked to quote on a rewire for a 1 bed flat. The cutout and prepayment meter is in the shop below. (1 cut-out - henley blocked into 2 supplies) The flat and shop are owned by different people - but the shop owner allows the folks from upstairs to come into his shop, go behind the counter and top up their electricity. Understandably, the owner of the flat wants this changing, as he doesn't think that the shop owners are always going to want his tenants doing this. Is this set-up even permitted? Given that the flat tenants can't access the main fuse (or their own meter) anytime the shop is closed?
Further more, the sub-main supply up to the flat is via an old switch fuse, into a 10mm T&E.
They have 9.5kw shower, Ceramic Hob and an immersion heater!
To start with, I'm thinking of advising the sub-main be changed to 16mm SWA from switch fuse, with separate 10mm earth - any thoughts on this? (total run is 5m)
Many thanks
Last edited: