looked at a job today in a small outbuilding where the RCD has been tripping after heavy rain. On IR testing I've isolated the fault to the ring main and specifically the part of the ring at one end of the building where there are some obvious signs of damp in the solid stone/brick wall.

So I removed the sockets and sure enough there is damp in the metal back boxes and some drips of water off the ends of the cables. So I IR'ed the buried cables (direct into the wall) on their own and was still getting very low readings (between 0.1Mohms and 23Mohms depending on the part of the ring that I tested).I would have thought that by removing the sockets and cleaning up the ends of the cables a bit I would have got slightly higher readings? - I'm assuming that the T&E cable should be impervious to water or am I wrong on ths point?.

Was going to recommend a rewire of the affected part of the ring using surface wiring and sockets with plastic boxes. Should this solve the damp problem?. any other ideas welcome.

thanks - Michael
 
Selection and erection guidance note states that PVC cable can absorb water over a period of time and is not impervious....it was talking about total immersion though........I'd go with telectrix's suggestion,the environment does not sound suitable for a flush install.
 

Reply to damp problems in the Talk Electrician area at ElectriciansForums.net

Similar Threads

  • Article
This is an RSS feed of thread: Gas or Water Pipe? Look to find cause of damp in wall. Content of the thread: Hi all, First time post so please...
Replies
0
Views
126
  • Question
There is no homework, and I'll never see these photo again.
Replies
3
Views
516
S
  • Article
Shower screen reinsert problem Hi I had to remove the glass panels from this quadrant shower cubicle and I'm struggling to get one of the screens...
Replies
0
Views
161
Sandy283
S
  • Question
Recommend this: Electricians Guide to Inspection and Testing Book -...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks