Plonker 3
Got a DB change to carry out in a house. 60/80 amp incomer, PME supply. Mains tails buried in walls but are double insulated. Main earth 6mm and bonding in 6mm.
The tails look in good condition. So don't want to change them as they are buried in the wall and cause unnecessary mess, but I think I need to change the 6mm main earth, but not the bonding would this be correct or am I being a bit thick in this thinking?
Took a quick Zs at the db when surveying and it was 0.14 ohms