Hi al

question !!!!

DB1 in house ( dual rcd ) feeding small ccu in garage with swa !!! this in turn will feed a swa to a garden shed!!!

Question !!!

i fully under stand 30ma rcd,s in line is a no no !!! so can i install the garage unit with just a main swith and no rcd/main switch and in turn feed the shed via swa from ccu in garage !!!

Question !!!

because of feed from db1 being on a rcd i can not tt the garage ccu so will have to export the earth from db1 . iunderstand you can do this as long as there is no extranios conductive parts in out buildings also i am going to rely on the rcd in db1 ( house ) to protect all the out side installation!!!! i know that if a neutral earth fault occures it will knock half the board out in db1 but can not see any other way round it !!!

Question !!!!

would you guys and girls approach it in the same manner

thanks
Richard
 
You could feed the garage from an unprotected way in DB1. As you are using SWA there's no need for RCD protection. Just earth the armour of the SWA at supply end only.

You could then fit RCD to garage CU and TT it. Then feed your shed from garage CU.

This would save you knocking half the house circuits out in the event of a fault.
 
Hi al

question !!!!

DB1 in house ( dual rcd ) feeding small ccu in garage with swa !!! this in turn will feed a swa to a garden shed!!!

Question !!!

i fully under stand 30ma rcd,s in line is a no no !!! so can i install the garage unit with just a main swith and no rcd/main switch and in turn feed the shed via swa from ccu in garage !!! Yes,as long as there is RCD protection it can be at either end.

Question !!!

because of feed from db1 being on a rcd i can not tt the garage ccu so will have to export the earth from db1 . iunderstand you can do this as long as there is no extranios conductive parts in out buildings also i am going to rely on the rcd in db1 ( house ) to protect all the out side installation!!!! i know that if a neutral earth fault occures it will knock half the board out in db1 but can not see any other way round it !!! It will not knock out the entire installation therefore it will comply with the 17th.

Question !!!!

would you guys and girls approach it in the same mannerI would prefer to feed of an unprotected way and RCD at the garage,but if this is not practical your plan sounds fine.One advantage with feeding from the house RCD is that it will be immediately apparent if it trips.If there are freezers in the shed/garage and the rcd is at that end it may not be noticed until it is too late.

thanks
Richard

Hope this helps
 
It will not knock out the entire installation therefore it will comply with the 17th.

The 17th simply requires that inconvenience is minimised in the event of a fault. It doesn't say that front-end RCD protection is never acceptable or that simply not taking absolutely everything out will necessarily comply.

I think a risk-based approach is really what it is calling for (i.e. a risk assessment) before putting a front-end RCD on a distribution board or whatever is intended.

That said, I don't think an RCD-protected distribution circuit in the instance mentioned would be a particularly wonderful design.
 

Reply to db1 to db2 to shed in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
155
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
983
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
Thank you so much for that! When I went to do the Ze at the DB, I tripped the RCD in the CU in the house, I understand that's a hard question...
Replies
2
Views
265
I don't really know if he is or not, but I would have thought an electrician would be able to calculate cable size or know about requirements for...
Replies
8
Views
679

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top