Dear all,

I need to supply DC 24V power to long distance. The required power is low up to 9W. What is the maximum allowable voltage drop?
 
in the absence of anything i can find, as you load is so small, less than 0.5A, just depends on the run. alarm cable with 2 cores paired will carry that for 50-60m, no sweat. what cable type are you considering?
 
panel mounted 24vdc power supplies sometimes have an adjustment pot. on the front, you may be able to adjust it up to 28vdc, Schnieder Electric make these
 
Indeed.... the current is very low 350mA. The distance is quite long.. up to 175meters. If I keep the voltage drop to 4% or 5%, than everything is fine because the cable is going to be 2.5mm2 which is the maximum allowable cable cross section of the controller board. What kind of cable is that? two core cable or two conductors of single core?

If I have to decrease the voltage drop, then the acceptable cable length is more than 10mm2. I am not sure buti n that case, I need to drop an AC cable, and then converted to DC.
 
Indeed.... the current is very low 350mA. The distance is quite long.. up to 175meters. If I keep the voltage drop to 4% or 5%, than everything is fine because the cable is going to be 2.5mm2 which is the maximum allowable cable cross section of the controller board. What kind of cable is that? two core cable or two conductors of single core?

If I have to decrease the voltage drop, then the acceptable cable length is more than 10mm2. I am not sure buti n that case, I need to drop an AC cable, and then converted to DC.

you can only run single core single insulated if it's in containment. depending on the risk factor as regards mechanical damage, you could use T/E or SWA.
 
you can only run single core single insulated if it's in containment. depending on the risk factor as regards mechanical damage, you could use T/E or SWA.

If the cable is 2.5mm2, can't be a conductor with two cores?

All the cables are going to be buried underground, so SWA is necessary.
 

Reply to DC 24V - Cabling Sizing - in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Depending on the specific battery you (intend to) buy, you might be able to just do Monster alternator -> LiFePo4 battery. The BMS for the fancy...
Replies
5
Views
358
  • Question
Hello I am going to use this pin connector to power a HDPLEX HIFI DC-ATX 500 watt power supply. The power supply has a 8 pin dc input connector...
Replies
0
Views
135

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top