J
jonnyboy1
hello lads
now im pretty new to the solar game but know what im doing, anyway after recent discussion today im wondering your thoughts on cliping both dc cables in a 2.5 twin clip together
is this acceptable or not?? one would think no for serval reasons but as the cable is double insulated its a pro to the argument.
if anyone could enlighten me on the matter it would be appreaciated
cheers
I can't see it being a problem if they both fit the clip size correctly.
However, I'd personally prefer to see black clips for black cable, whether they're both clipped together or individually.
Or use conduit / flexible conduit.
Can I ask if it is ok to run AC & DC cables in the same trunking or bundle. For instance if there is an existing ceiling track with a bundle of AC cables attached to it is it ok to add DC cable to the AC bundle?
Thanks.
I would also like to know that. I did look some time ago and could not find one. The 'requirement' comes from a tick box on the standard PV Commissioning Test Sheet in the DTI Guide which says 'segregation of ac and dc cables' or similar.
As far as I'm aware, BS7671 refers to segregation and separation as two separate and distinct conditions.
Separation is achieved by keeping cables a distance from whatever it is they are to be separated from, such as 50mm from service pipes etc.
Whereas segregation can be achieved by use of insulation, as long as the minimum rating of insulation of a cable is greater than the highest voltage in any of the cables, segregation is achieved.
There appears to be nothing in Section 712 of BS7671 indicating a requirement for separation.
There is the answer ...........................the IET say one thing and the DTi as usual say something else
I do not have a computer searchable verion of 7671, but neither separation or segregation are defined on their own and the term separation is normally used in the context of electrical separation (viz shaver socket).
Looking again at 7671 perhaps the requirement comes from 515.2. Whether physical segregation by barriers/distance is required in addition to the double insulation then becomes a matter of judgement based on perhaps lightning risks.
Yes, it is the case that BS7671 does not define either segregation, or separation.
However there are a number of Sections and Regulations that refer to both segregation and separation.
For instance Section 444.6 (segregation of circuits) refers us to Regulations 528.1-2 in order to provide segregation for cables of voltage bands I & II.
Regulation 528.1 indicates one method being: "(i) Every cable or conductor is insulated for the highest voltage present".
Following the amendment, we now have Annex A444, with Tables A444.1-2, which indicate that segregation can be achieved by means of separation.
As for Regulation 515.2, all that requires is segregation be provided, there is no indication of a preferance for a particular method of providing the segregation.
To my mind, there are a number of methods to provide segregation, separation being just one method.
Just as there are a number of methods for providing additional protection to cables concealed in walls, 30mA RCD protection being just one of them.
Thank you for digging that lot out. I suspect you are into a level of detail beyond that which the average mcs annual audit candidate and annual audit assessor will care to get their minds around.
What they want pehaps is an answer to the question what quick, standard, simple measures can I take so I can tick that box on the commissioning sheet?
I see where your coming from here Bruce, but I'm sure you know i'm very much against these "belt & braces" approach to our industry, for IMO it is just dumbing it down .
Yes there are places for guides and to make life easy, but the DTi in my opinion are trying to create a one size fit all system, and cater for a workforce in the industry to be, for no finer point semi-skilled.
For me the package of being an Electrician is design, installation and testing, once you start to take away the training to do this, your just creating what we have now, an industry, not just PV, but the electrical one as a whole, that really is poor, producing literally "electricians" that know what to do because they have a guide that tells them, but not WHY we do
Drifting off thread.... I agree with you, I was just reflecting what I think is the current situation. So often I read here and elsewhere people seeking proforma solutions rather than being able to understand and think through the problem they are trying to solve. Regular debates on the difference between fault/overload currents and fault/overload protection spring to mind.
Earthing and Bonding is the real classic, apart from identifying the difference between which is which and what does what, sizing it, do we need it, can we do this with it ............................you would think it was quantum physics
6242Y (twin and earth) is rated at 300/500V, considering a string can easily exceed that then there's a good reason for segregation of the two circuits.
Segregation is associated with Band I and Band II circuits and Band I circuits are normally, and certainly in this case classed as ELV.
So regardless of what T+E is rated at anything over 50v and up to 1000 volts, again in this case, would be band II, so regardless of what the DC voltage is as long as it's below 1500V DC it is class II
Having not worked with Dc other than PV and on canal longboats is it common practice to run unshielded Dc circuits with Ac in trunking/tray etc in industrial installations ?
I did some work in a quarry a few years ago and noticed that the few Dc circuits they had were kept well apart from the Ac circuits and did look for a reason for this , I thought it would be due to the Dc cable being unshielded and induced voltages etc but the Ac were all SWA , the only thing I found was via internet search which was a reference to an English translation of a German VDE regulation which did mention this practice in certain instances .
I'm not keen on the idea of clipping the cables side by side in domestic scenarios simply from the view of accidental damage causing arcing etc, although you then have to think about creating loops if you keep
-ve /+ve apart I usually run the cables in conduits, or if clipped run in areas which are not prone to damage like on the outer side of purlins , and I think its a good idea to put warning labels on the more visible side as well as next to the cables just in case someone starts knocking nails in.
Hi every one can I run DC cables together with earth cable in one conduit from the roof? Dos earthling cable has to be connected to the panels frame or in to the railing will be fine as per picture?
DC cables
Thread Tags
jonnyboy1,
valet,