Just wondering what other installers' thoughts are regarding DC and armoured cable.

I have an install coming up where we have a fairly long cable run. I would tend to install the inverter at the array and run a long AC cable back to the CU. I know some people have actually run the DC cables back to the CU itself and installed the inverter there. To me this seems like a bad idea as there is the potential for shorting out the steel wire armouring down to the DC, which would introduce a DC current to the main earth.

I'd be interested to hear any thoughts.
 
Reasons for putting dc through a long swa cable:
- dc voltage likely to be higher than ac voltage, therefore current lower, therefore power loss lower for same size of cable.
- no problem with ac voltage drop causing exterior inverter to cut out due to over-voltage. More important with G59 as allowed over-voltage is lower.
- if there is an earth fault in the dc cable, then it would be detected by the inverter RCMU and shut down. Low level earth faults would not be detected on an ac cable unless rcd protected.

Reasons for not doing so:
- none really
 
- if there is an earth fault in the dc cable, then it would be detected by the inverter RCMU and shut down. Low level earth faults would not be detected on an ac cable unless rcd protected.

Fair enough, the inverter would shut down. But the fault to the earthed bonding on the SWA would remain. Surely this is not desirable?
 
It puts a dc potential onto the earth in the case of a fault, but unless there was a second fault somewhere that provided a dc circuit then it would not cause any current to flow. So a single dc fault is not immediately dangerous.

There are others here who routinely operate in the commercial field who might have a view.
 
Fair enough, the inverter would shut down. But the fault to the earthed bonding on the SWA would remain. Surely this is not desirable?
as bruce says, it becomes a separated circuit with no return path, so no danger. We've probably used SWA on the DC side of around 50% of our installs as we prefer to run the SWA down the outside of the house from the roof, and I prefer the mechanical protection this gives.
 
Thanks for the info.

I suppose it is no different to installing on a metal roof which is deemed to be extraneous and therefore bonded. Just doesn't seem right. Wanted to run it by others to see if they flagged anything up. For this installation, it is desirable as we have no means of practically housing an inverter near the array.
 
Couple of questions here.
1 Does the DC cable need to be earthed?
2 If so, can you not TT it the "extraneous" end, keeping it completely separate from the AC therefore removing any potential for DC entering AC?

Only trying to help here?
 
Couple of questions here.
1 Does the DC cable need to be earthed?
2 If so, can you not TT it the "extraneous" end, keeping it completely separate from the AC therefore removing any potential for DC entering AC?

Only trying to help here?
1 - arguable, we don't earth it on isolating transformer inverters because IMO it's safer not to as it's an isolated circuit, but do on TL inverters after a debate on here IIRC about it when I realised there was some logic to it.

2 - Sounds like a bad idea to me to introduce an alternative earth path, plus I've no wish to have to go banging earth rods in again if there's not a very good reason for it.
 

Reply to DC through armoured cable in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar threads

I assume said contractor is part of a Part P scheme (NICEIC, Napit, few others..) in which case complain to them. They'll investigate (in theory)...
Replies
10
Views
802
  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top