When working with discontinued products there is always a problem working out what to do, looking at TLC website both the
MCB and the
RCD are discontinued. One would need to contact Contactum to find if there is a replacement.
I know we all tend to simply look for some thing that will fit, however the reason it's called a consumer unit, not distribution unit is it's type tested, so we are not permitted to fit anything which was not type tested with the unit, I have seen it done many times, but would not make a video showing it being done.
So options are a consumer unit which is up to date, with a MCB/RCD/RBCO which is designed for the unit, be it on henley blocks as separate unit, or complete change, or combine some ring circuits and use the existing 32A MCB which means a shower that uses under 32 amp.
I know it's a pain to change the consumer unit, but that was really the only way forward, anything else is a bodge. Likely I would also bodge, however I would not make a video of the bodge.
It does not show the DNO fuse, if the DNO fuse is 80 amp or less, then there is nothing wrong with a 80 amp RCD being fitted, this house has a 60 amp DNO fuse, and twin fuse box/consumer unit so some thing like 20 ways. Power use has dropped with LED bulbs and induction hobs etc.
But it has never been correct to fit a 80A RCD with 4 x 32A MCB's with a supply over 80A, however what one does not know is was the supply fuse over 80A when the board was fitted? So you have no idea who was at fault.