Earlofdon

Hi folks I'm new here so please forgive me if I'm posting in the wrong place etc
Am hoping someone can help.

I need to remove old wiring to a downstairs electric shower. The shower was removed sometime back with the wiring to the switch remaining!
Anyway 247 volts showing at the switch.
Turned circuit off at circuit breaker fuse box
Zero volts at switch.

I needed to cut the cable in order to facilitate its removal.
The circuit breaker for All sockets tripped out.
Reset it and tried again but circuit breaker tripped again - thankfully!

Please, any advice gratefully received.

Regards,
Chris
 
Hi Earl, welcome to the forum.

When you disconnect a circuit by switching off the circuit breaker you're only disconnecting the live wire. The neutral and earth are still connected and shorting them out by cutting them will cause an earth leakage fault which will trip the RCD which may also be supplying other circuits therefore causing them to have power outage.

Are you an electrician or is this a DIY endeavor? What test equipment do you have?
 
Hi Earl, welcome to the forum.

When you disconnect a circuit by switching off the circuit breaker you're only disconnecting the live wire. The neutral and earth are still connected and shorting them out by cutting them will cause an earth leakage fault which will trip the RCD which may also be supplying other circuits therefore causing them to have power outage.

Are you an electrician or is this a DIY endeavor? What test equipment do you have?
I think its blindingly obvious that he's not an electrician.
 
Agreed, as Richard suggests remove the entire cable first by disconnecting the live, neutral and earth wires then pull it out of the CU entirely. You'll need to switch off the power at the CU main switch and it would be very advisable to prove it dead with a tester first. If you're not familiar with the layout of a CU or not comfortable with you skills being up to the job then rather call a professional to assist.
 
Hi folks I'm new here so please forgive me if I'm posting in the wrong place etc
Am hoping someone can help.

I need to remove old wiring to a downstairs electric shower. The shower was removed sometime back with the wiring to the switch remaining!
Anyway 247 volts showing at the switch.
Turned circuit off at circuit breaker fuse box
Zero volts at switch.

I needed to cut the cable in order to facilitate its removal.
The circuit breaker for All sockets tripped out.
Reset it and tried again but circuit breaker tripped again - thankfully!

Please, any advice gratefully received.

Regards,
Chris
the DIY section is over there..

alternatively..get an electrician in..
 
I think its blindingly obvious that he's not an electrician.

mick,where have you been these last few years,the obvious may not be so obvious with the new recruits these days
[ElectriciansForums.net] Dead Circuit Tripping Circuit Breaker
 
Thanks for the replies
No, I'm not an electrician!
Apologies for being thick but do I have to switch off the mains power completely before removing cable or could I switch off the sockets circuit breaker which was the one tripping out?
 
No definitely play it safe and switch off ALL the power at the main switch. It would be better to do the removal of the cable in daylight and if you're unsure what you're doing call a local electrician, the job will take literally a couple of minutes for someone who knows what they're doing. It isn't worth the risk if you're unsure about anything.
 
No definitely play it safe and switch off ALL the power at the main switch. It would be better to do the removal of the cable in daylight and if you're unsure what you're doing call a local electrician, the job will take literally a couple of minutes for someone who knows what they're doing. It isn't worth the risk if you're unsure about anything.

Thanks again.

The cable goes all the way into the loft and is connect to some round thingy with other cables going in and out, like a sort of junction connection

was just going to pull in up and tape off the ends and leave in the loft
 
Thanks again.

The cable goes all the way into the loft and is connect to some round thingy with other cables going in and out, like a sort of junction connection

was just going to pull in up and tape off the ends and leave in the loft

It needs disconnecting from the junction box - sticking tape on live wires (once switched back on) is a disaster waiting to happen.

The electric shower obviouslly hasn't been on it's own circuit if it's in a junction box with other cables. Make sure the consumer unit is completley isolated then remove the electric shower cable from the junction box - and remember to tighten down all the other connections back properly afterwards, otherwise more problems can arrise.
 

Reply to Dead Circuit Tripping Circuit Breaker in the DIY Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
325
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
852
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
973

Similar threads

Ok, please be aware that I am a 'do-it-yourself-er,' so if this isn't the right place to be posting this thread, let me know where I should be...
Replies
0
Views
452
  • Question
It sounds like there is damage to the wiring underground. Do you know what kind of cable was used, in any underground wiring is used has to be UF...
Replies
3
Views
651

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top