Hi.
I am after a bit of advice if anyone can help. I got called to a job due to RCD tripping. Ir circuits and fault was on cooker. Disconnected cooker and fault gone from DB. The landlord tried to get the cooker fixed , but appliance engineer couldn’t fix, so he brought a new cooker. Today he had cooker installed but when it was switched on it tripped the rcd. I went back and the cooker was disconnected and I found no fault from the DB, however when I did an ir from switch back to DB I had a dead short neutral to earth. It’s a flat so can’t pull boards up from upstairs so am going back to run a new leg of cable. Has anyone got any idea why it would show a good ir from DB to switch but not the other way around.
Thanks in advance
Steve
 
If the cable is continuous the IR will measure the same from all points. If the cooker worked we can assume the neutral is continuous, but did you check the CPC continuity? A nail or screw through the cable could just possibly sever the CPC and short the switch side of the break to the N, leaving the DB side disconnected.

Another explanation is that the fault is intermittent and located near the switch, where any movement of the cable can make or break the contact. It actually reads the same IR from both ends at any one moment, but the act of opening and moving the switch to carry out the test can provoke the fault to come and go, so you get different results each time you test.
 
Scenario: drill a hole through a cable due to muppetry, bang. Remove drill bit / screw = you now potentially have a broken conductor from the supply side and a shorted conductor on the load side.
 
If testing back towards the board, you need to isolate at the origin if testing between E and N.

remember that N is connected to E somewhere. For TNC-S it is connected at the property, for others it’s done at the substation, but they are always connected on the supply side.
 

Reply to Dead short neutral to earth in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
936

Similar threads

  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
764
Yup will do exactly that when I'm back down there. Thanks for the help
Replies
6
Views
382

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top