newtothis

Testing using a socket tester at the sockets gives me unexpected readings, based on little r calcs,
eg, outside allowed variance
Using the probes on the terminals gives me 'Texbook' readings expected from a new install.


Should I conclude the accessories are dodgy ?
They are DP double gang sockets costing £1.90 from TS

Thanks for any help, Please let me know if anything I've said that sounds stupid.
I'd rather know,,,, I have a thick skin ;)
 
What sort of variance levels are they?
If you are talking 0.1Ω then switching the switch back and forth and taking the socket tester in and out of the socket a few times may help clean up the contacts. (I often think I need a plug with fine sandpaper on the pins for this purpose!)
If you are talking 1Ω then the sockets are probably rubbish.
 
Testing using a socket tester at the sockets gives me unexpected readings, based on little r calcs,
eg, outside allowed variance
Using the probes on the terminals gives me 'Texbook' readings expected from a new install.


Should I conclude the accessories are dodgy ?
They are DP double gang sockets costing £1.90 from TS

Thanks for any help, Please let me know if anything I've said that sounds stupid.
I'd rather know,,,, I have a thick skin ;)

https://www.youtube.com/watch?v=zSATFrqlSpg
 
Have you carried out "end to end" r1, r2 & rn dead tests at the board/CU? That is where you should start.
Yes did that before I connected them to the CU did end to end on each one.
Then figure of eighted r1 + rn tested at every socket same with r1+r2.
did the calc r1+r2 /4 got 0.31

When I removed the socket covers every socket was 0.32 Ohms.

What sort of variance levels are they?
If you are talking 0.1Ω then switching the switch back and forth and taking the socket tester in and out of the socket a few times may help clean up the contacts. (I often think I need a plug with fine sandpaper on the pins for this purpose!)
If you are talking 1Ω then the sockets are probably rubbish.

when I went to the sockets they were from 0.31 to 0.70 Ohms
Rocked them about abit.

Sometimes I get confused by decimal fractions, is this the case here ?

https://www.youtube.com/watch?v=zSATFrqlSpg
Thanks I will revew that.

I carried out IR tests result both >999 for L-N & E-L and N-E 780 mega ohms
I am curious to know why N-E was lower but not too worried.
 

Reply to Dead tests on a ring final prior to energising in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
350
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top