i have been asked to install a rewire into a house including a new consumer unit. the customer would also like power run to a shed which i have never done before. my instinct says i would need swa as he doesnt want high or underground cable. it is only to supply a shed c.u for sockets and lights so am intrigued to find out my options from you professionals! any advice appreciated
and how many points will be in this shed?.....whats the intended use?.....whats the earthing arrangements here?....any water or gas extrainious conductive parts in this shed?.......check both earthing and bonding arrangements here first and upgrade/replace to the 17th edition standard before doing any work here....how longs the run from the origin of supply for this shed and the shed itself?....
so i would suggest a 16A MCB (for the outlets).....and a 6A MCB for lighting......need to know the earthing arrangements though mate as this will determine whether an s type RCD is required (for discrimination purposes)......
TBH I would bury SWA, out of sight, out of mind. As you're doing a complete rewire, run T+E under the floor space if you can, adaptable box onto SWA and off to the shed you go. Buried looks a hell of a lot tidier, if not, is there anything for you to clip the cable to?
The key word I`m afraid is professionals. I take it from this that you dont consider yourself a professional which begs the question should you be undertaking any of the work in the first place?
are you qualified/ competent/ experienced to complete this work? Are you notifying this work or have you contacted building control?
I have noticed that these posts are becoming less frequently responded to by the regulars for good reasons.
To be honest, I suspect that if you were competent to be undertaking this kind of work, then there would be no need to ask this type of question as you would be familiar with the requirements for electrical installations BS 7671.
Hence I will offer no further advice unless specific and understandable questions come forthwith.
Get a registered and experienced electrician.
Reply to decision to make in the UK Electrical Forum area at ElectriciansForums.net
Thank you for another very helpful response. Just to assure you we are saying the same thing, I was referring to the 2.5 on 20A radial which I now...
Given that, it probably makes sense to TT the shed, unless you can be sure it doesn't act as an extraneous-conductive-part. (The SWA won't have...