Carrying out an EICR and came across a ring final circuit wired to the first of six metal clad sockets in 2.5mm 5 core SWA. Obviously 2 cores for live, 2 for neutral & 1 fir the CPC. No earth tag at either end of the SWA so can assume it's not being used as a CPC. Should I put this down as a departure or C3.
 
Carrying out an EICR and came across a ring final circuit wired to the first of six metal clad sockets in 2.5mm 5 core SWA. Obviously 2 cores for live, 2 for neutral & 1 fir the CPC. No earth tag at either end of the SWA so can assume it's not being used as a CPC. Should I put this down as a departure or C3.
The armour should be Earthed. But for the lack of ring continuity on the cpc then I would suggest that this needs to be rectified.
 
If a core is being used as the CPC, and they earth the armour, what is the departure?
 
If they earth the SWA correctly either end while I'm here wouldn't it just go down as a departure?

No, you don't record departures on an EICR, that is something that you record on an installation certificate.

An EICR is only concerned with reporting on the suitability for continued use of the installation by recording non-compliances which have a safety implication or that could be changed to improve the safety of the installation.

A ring circuit is required to have a CPC in the form of a ring unless it is formed by a metal covering or enclosure containing all of the conductors of the ring (543.2.9)
So as it is now I'd be inclined towards C3 but if the armour is properly connected at each end (and 543.2.7 has also been complied with) then no code.
 

Reply to Departure from BS7671 or C3 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar threads

Came across 3No 1ph heaters connected by 2xT&E cables from a 3phase supply on an installation whilst carrying out an EICR few years back...
Replies
9
Views
678
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top