Departure or not? | on ElectriciansForums
Discuss Departure or not? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Amp David
Mentor
Glossop
Minor Works Cert, Details of Departures Section.
Would the lack of an RCD go in here although when installed it wasn't a requirement?
Simple question, from a simple guy:eek:
If your work required rcd protection then you should provide it because regardless of when the existing work was installed, you install to BS7671:2008.
In amendment 1 there is provision for omitting an rcd on minor works subject to risk assessment but you'll have to wait a good while for that.
Like for like would not require upgrading....in which case a lack of rcd protection could be noted in the 'comments on existing' box....a departure would only be the case if the work you carried out did not comply.
Reply to Departure or not? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Unless the circuit is new or has recently been tested/certified by a.n.other, I'm not sure how you prove the circuit is 'safe' to connect to...
I usually put something like this To assess compliance with BS7671 for continued safe operation (5 year periodical inspection)