been to a property to day that has had the loft fully insulated 150 mm deep on top of the existing insulation.question is what code to give it

1 imidiate danger
2 needs improvement as it poses no emidiate danger

I would go for 2
any remarks
 
What size is the cable? If 1.5mm it may be okay, you need to check the de rating factor. It used to be 50% for cables fully enclosed in insulation with runs greater then 500mm but not sure without checking the BRB.
 
i'd either calculate the load and whether the cable ( derated) is overloaded or not. if not-- no code. or, give it a code 3 as requiring further investigation.
 
Or you could do what I would say quite a lot of guys do and put "attic space not inspected":drunk:


On a more serious note, do the sums calculate the applicable factor and see where you are then.
 
soory yes it is a kitchen ring whch has 2 x 2.5mm spured

I have sugested droping the circuit to a 20A and raising the spured cable above insulation as the cable as installed >100mm of insulation is 17A which leaves the cable still unprotected by the 20A ocp
all heavy loads a seperatly supplied
 

Reply to derated cables in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
93
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
889
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

The cable is way undersized. If the voltage drop is detrimental to the installation I would make a mention of it as volt drop generally is not...
Replies
2
Views
390
  • Question
This is an interesting issue. I agree with you however I took this to task with a scam inspector some years ago and we agreed to disagree that...
2
Replies
29
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top