Derating cables laid on top of loft insulation | on ElectriciansForums
Discuss Derating cables laid on top of loft insulation in the UK Electrical Forum area at ElectriciansForums.net
Dronfield
Hi All, opinions please, just been to a property that has a 6mm cable ontop of 200mm of loft insulation so not buried. What de-rating factor would everyone apply to this
Would it help if i could get it in some big trunking?
I would not be de rating cable being on top of insulation, but it should be adequately secured along its length.
If this is a loft, you might need to de rate for ambient temperature.
I imagine it must pass through the insulation at some point so 0.68 off the top of my head.
These
Clipped direct, with adjustment for ambient, or through insulation (depends on thickness @ that point(s) ) or whatever the rest of the run is whichever is the largest de rating
Laid on top then I personally would not apply any correction factor
laid underneath for most of the run then its about 0.6 or something
Laid underneath would depend on the amount of insulation ie T&E above a plasterboard ceiling covered by thermal insulation not exceeding 100mm would be reference method 100, exceeding 100 mm would be 101, from there you would look at the appropriate table in appendix 4 for the ccc of the cable.
You may need to apply further correction factors where applicable.
Thanks all for your thoughts.
As i said cable is on top of insulation and not underneath.
Very hard to clip to anything as there is no slack to move cable so basically just sits on top.
Wonder if there is any merit in placing in some big trunking, 50mm x 50mm, but again what reference method would this be classed as?
Just leave it clipped above, installing it in trunking would be reference method B and will reduce the ccc , further to any other factors.
The question is does it penetrate the insulation and thus become totally enclosed by insulation. If less than 0.5m then derating will have to be applied. Unless it goes past the insulation and down to (say) the shower.
Sounds to me like it’s a problem for the donut who decides they needs another 100mm of insulation on top....be unusual if it doesn’t pass through the existing insulation at least somewhere though......
Reply to Derating cables laid on top of loft insulation in the UK Electrical Forum area at ElectriciansForums.net
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
Hi I'm again struggling with a long overdue 2396 project but, as before, am at a standstill when it comes to the lighting design. Please could...