Does anyone know which table I should be looking in to calculate the current carrying capacity of 4mm PV cable and also how to do the derating calc for the Non conformities in my MCS inspection?

I installed a 6 panel Mitsubushi system with the +ve and -ve legs of the string measuring 15m each, run in PVC conduit.

Two of the points this installaion was pulled for are

1/ No DC Cable de-rating factors available to view as per DTI guide 2/. No DC Cable volt drop calculations available as per DTI guide

All I've got is:
The Voc = 30.6v x 6 x 1.15 = 211.14v stc
The Isc = 8.13 x 1.25 = 10.6 Amps (as there's only one string!)
Segen used PV Sol for me and calculated 0.83v volt drop

I'm embarrassed to say, I dont know which table I should reference in 7671. I asked Napit and they weren't sure!
Please Help!

Regards Paul


 
Ohms law works for dc and ac. When you are doing the calcs or using tables for ac you are dealing with rms voltages and currents. So the same calcs and tables will work for dc.
Regards
Bruce
 

Reply to Derating factors and current carrying capacity of pv cable in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
382
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
963
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
265
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top