A

Alessandro

Hello,

I have a problem with design current (Ib) and selection of the circuit breaker (In).
If I have a circuit of 7A and I apply no diversity, then Ib = 7A and I select a 10A circuit breaker.
But if I apply diversity and I get, say, 5A, is 5A now the design current Ib? So can I select a 6A circuit breaker?

Another problem: On-Site Guide says that for domestic cooking appliances I should consider the first 10A plus 30% of what's remaining. So if I have a cooker with 35A current demand, after diversity the current demand of the circuit is 10A + 0.3 * 25A = 17.5A. If this is the design current, then I select a 20A circuit breaker. But now this half of the full load current demand (35A), and if someone uses just 60% of the current demand the circuit breaker will trip.

Last question: if I have discharge lighting, let's say 5A, then I should probably use a type C 6A circuit breaker. But if I multiply by the factor of 1.8, 5A * 1.8 = 9A. Should I use a type B 10A circuit breaker?
Are both valid options?

Thank you. :)
 
taking the cooker example. if your design current is 17.5A after applying diversity, you could use 2.5mm cable., but only if not derated. then you would select the OCPD rating In such that Ib<In<Iz. however to allow for derating and possible future proofing against a bigger cooker being installed, you'd would go up a size to 4mm or even 6mm and select OCPD accordingly. then consider volt drop and Zs. these would both factor into your calculations.
 
............Last question: if I have discharge lighting, let's say 5A, then I should probably use a type C 6A circuit breaker. But if I multiply by the factor of 1.8, 5A * 1.8 = 9A. Should I use a type B 10A circuit breaker?
Are both valid options?

Thank you. :)
With discharge lighting you can have a high starting current for as long as 15 minutes depending on lamp and ballast type so whatever OCPD you chose it should be able to accomodate 1.8 times the run current for that length of time. Whether you could use a C curve MCB or not would depend on your Zs and whether required disconnect times would be met under fault conditions.
 

Hello :)

I have a problem with design current (Ib) and selection of the circuit breaker (In).
If I have a circuit of 7A and I apply no diversity, then Ib = 7A and I select a 10A circuit breaker.
But if I apply diversity and I get, say, 5A, is 5A now the design current Ib? So can I select a 6A circuit breaker?

Yes (5A is now the design current) and yes, you can select a 6A circuit breaker.

Another problem: On-Site Guide says that for domestic cooking appliances I should consider the first 10A plus 30% of what's remaining. So if I have a cooker with 35A current demand, after diversity the current demand of the circuit is 10A + 0.3 * 25A = 17.5A. If this is the design current, then I select a 20A circuit breaker. But now this half of the full load current demand (35A), and if someone uses just 60% of the current demand the circuit breaker will trip.

If you've got a copy of the regs, have a look at figure 3A4 on page 325 (appendix 3). This shows the time-current characteristics of type B circuit breakers. For a 20A breaker, the trip time for and overload current of 35A is about 400 seconds (6m40s). By that point, at least one of the thermostats, probably more than one, will have kicked in, reducing your load and increasing your trip time. So in practice, unlikely to be a problem.

Last question: if I have discharge lighting, let's say 5A, then I should probably use a type C 6A circuit breaker. But if I multiply by the factor of 1.8, 5A * 1.8 = 9A. Should I use a type B 10A circuit breaker?
Are both valid options?

See Marvo's post above.

Thank you. :)

No problem :) Good questions.
 
Thank you guys, fantastic answers. :D
I think that I have a decent grasp of design now. Just starting inspection and testing, expect more questions. :D
 

Reply to Design current and circuit breakers in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
929
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top