timo

When working out design current i know its P/V = Ib but how do you work this out for sockets?

Is a ring main just 32A

But what about a Radiel that feeds say 4 sockets, 1 spur that feeds 3 light points?

Many Thanks in advance

Timo
 
you use your design current to work out your fuse rating and then cable size.
In the wiring you are talking of there are set assumptions, hence 2.5mm ring main on 32A breaker.

Please elaborate on your query, are you doing a theoretical calculation?
 
Cable calcs really. btw sorry im a newbie so still learning allot. :)

Okay i know you need to work out design current before you can chose the cable size and protective device. (along with factors such as insulation etc)

I can work a shower raidel out easy enough.
example

9Kw Shower =

Ib = p/v

9000/240 = 37.5A

Design current 37.5Amps and then a suitable cable to carry that current and then a suitable MCB to protect.

But im a little unsure how you would work out the design current on a socket raidel.

If you had a raidel with 3 or 4 sockets on it with 1 fuse spur feeding 3 100watt lights how do you work out total design current on that raidel.
 
Unless you know what is being plugged into the sockets you can't, hence the generalization 2.5mm 32A ring, 2.5mm 16A radial etc.

All you can do is work out the 3 x 100w lamps.

Unless as it is a theoretical college question where they want you to assume a max load per socket of 13A
 
so really it would be 16A as the design current.

Is this what you would use on your paperwork that you give the customer along with diagrams etc when you show your workings (cals) for each circuit
 
Sorry to sound like a **** but these are frighteningly basic questions to be asking.

Are you just starting an apprenticeship?
 
Last edited by a moderator:
Cable calcs really. btw sorry im a newbie so still learning allot. :)

Okay i know you need to work out design current before you can chose the cable size and protective device. (along with factors such as insulation etc)

I can work a shower raidel out easy enough.
example

9Kw Shower =

Ib = p/v

9000/240 = 37.5A

Design current 37.5Amps and then a suitable cable to carry that current and then a suitable MCB to protect.

But im a little unsure how you would work out the design current on a socket raidel.

If you had a raidel with 3 or 4 sockets on it with 1 fuse spur feeding 3 100watt lights how do you work out total design current on that raidel.


As we now work to a harmonised voltage you should be using 230 in the above calculation and not 240
therefore

Ib= 9000/230=39.13A
 

Reply to the thread, titled "Design Current" which is posted in Australia on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Daily, weekly or monthly email

Back
Top