A colleague has asked me if I would carry out the electrical installation for the detached garage that he has just had built.
The supply in his house is TN-C-S and his gas and water services are correctly bonded.
The garage is constructed out of steel stanchions buried in the ground with blockwork in-between, a metallic roof and then rendered on the outside.
He has already buried a 6mm² csa xlpe in-between the house and garage.
He is planning on having a radiator in there supplied from the house using copper pipework buried underground.
My concern is the two different potentials in the garage from the steel stanchions and the copper pipework which is already bonded back at the house.
I am thinking that there should be an additional 10mm² csa MEB ran in from the house to the garage, linking the steel stanchions and the radiator pipework where it enters the garage.

Does this sound ok?
 
A colleague has asked me if I would carry out the electrical installation for the detached garage that he has just had built.
The supply in his house is TN-C-S and his gas and water services are correctly bonded.
The garage is constructed out of steel stanchions buried in the ground with blockwork in-between, a metallic roof and then rendered on the outside.
He has already buried a 6mm² csa xlpe in-between the house and garage.
He is planning on having a radiator in there supplied from the house using copper pipework buried underground.
My concern is the two different potentials in the garage from the steel stanchions and the copper pipework which is already bonded back at the house.
I am thinking that there should be an additional 10mm² csa MEB ran in from the house to the garage, linking the steel stanchions and the radiator pipework where it enters the garage.

Does this sound ok?

New one on me never heard off a roof being rendered before:rolleyes4:

Sounds a really bad idea taking 2 pipes to the garage to heat it, how is he going to insulate them as they will lose most off their heat by the time they get to the garage. Suggest that if he wants to heat the garage to lokk at putting in a couple of electric heaters
 
Sorry, just meant that the walls had been rendered.
He is a heating engineer so i am not concerned with heat loss on his pipes etc. Just concerned with the electrical side
 
you may need to bond the steelwork to the pipes. make a EMT in the garage.. a 10mm back to the MET is not needed as your copper pipes are bonded back to the MET anyway.a rod added at the garage might be advantageous. ( i'm not 100% on this, and so stand to be corrected by E54 or someone. )
 
you may need to bond the steelwork to the pipes. make a EMT in the garage.. a 10mm back to the MET is not needed as your copper pipes are bonded back to the MET anyway.a rod added at the garage might be advantageous. ( i'm not 100% on this, and so stand to be corrected by E54 or someone. )

In theory you can use copper pipes as a bonding conductor, if you bond them to the steelwork then that acts as a rod anyway! Although you may want to test the Ze of the metalwork to make sure.
 
New one on me never heard off a roof being rendered before:rolleyes4:

Sounds a really bad idea taking 2 pipes to the garage to heat it, how is he going to insulate them as they will lose most off their heat by the time they get to the garage. Suggest that if he wants to heat the garage to lokk at putting in a couple of electric heaters

Sorry, I agree with you, what a mad idea! The worms will love it :jester:
 
Personally I would bond all metal parts as they enter the garage. Being a plumber, your mate will probably run his heating pipes in plastic anyway. If you equipotential bond in the garage then there will be no potential difference.
 
10mm bonding between main and garage cu, then bond this to the steelwork and pipework in 10mm inside the garage. For all you know, there may be a plastic coupling in the heating run, then your pipework will just become an ECP, along with the steelwork. Never rely on anything which could be removed at a later date to be your bonding.
 
Think you will find you can't export the earth from the main building as it TN-C-S you will have to only bring out the line and neutral from house, make the detached garage a tt system, then bond all extraneous parts to you new tt main earthing terminal. Ie structural steel and heating pipes. Job done!
 
Think you will find you can't export the earth from the main building as it TN-C-S you will have to only bring out the line and neutral from house, make the detached garage a tt system, then bond all extraneous parts to you new tt main earthing terminal. Ie structural steel and heating pipes. Job done!

Here we go again..... :)
 
Check the resistance between the steel uprights in the garage and the MET. As the stanchions are into the ground you may find that you have a ready made 'rod' with the garage steelwork which gives a good reading.

There is a term for it, but the word escapes me E54 or Tony will know I'm sure.
 
Think you will find you can't export the earth from the main building as it TN-C-S you will have to only bring out the line and neutral from house, make the detached garage a tt system, then bond all extraneous parts to you new tt main earthing terminal. Ie structural steel and heating pipes. Job done!

Anyone for pop-corn? :)
 
Think you will find you can't export the earth from the main building as it TN-C-S you will have to only bring out the line and neutral from house, make the detached garage a tt system, then bond all extraneous parts to you new tt main earthing terminal. Ie structural steel and heating pipes. Job done!

Think you will find that who ever told you that is an obsessive compulsive liar. :lol:
 
As it's a separate building and with a PME service at the head, you will need the separate 10mm bonding conductor between the MET and garage EMT in this garage to connect to the steel frame and to the daft copper heating pipes etc, if your intending on extending the house PME equipotential zone!! What sort of distances are we talking about here??
 
if the 6mm SWA is already in place and a 10mm bonding conductor would be a pain to fit, then TT the garage. bloody big rod and the steelwork should give a decent Ra. LOL.
 
Yeah it`s already in situ, beneath a block paved yard. His garage is still under construction but he is putting insulated plasterboard on the walls, tinted windows etc. Should be nice and snug when complete
 

Reply to Detached garage in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

  • Question
So this was resolved. I used a line tester to see if I had power across the breaker on the main box in the house. Breaker tested fine. Then I...
Replies
3
Views
1K
Not really its clear in black and white. Not knowing the regs isnt the regs books fault.
Replies
10
Views
755
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K
  • Question
Without specific information I could only a give belt and braces ‘cover all bases answer which will definitely be costing you considerably more...
Replies
1
Views
1K
I want to verify if the breaker size is correct for the service going into my detached garage. I have 6 AWG cable going from my main panel in my...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks