A colleague has asked me if I would carry out the electrical installation for the detached garage that he has just had built.
The supply in his house is TN-C-S and his gas and water services are correctly bonded.
The garage is constructed out of steel stanchions buried in the ground with blockwork in-between, a metallic roof and then rendered on the outside.
He has already buried a 6mm² csa xlpe in-between the house and garage.
He is planning on having a radiator in there supplied from the house using copper pipework buried underground.
My concern is the two different potentials in the garage from the steel stanchions and the copper pipework which is already bonded back at the house.
I am thinking that there should be an additional 10mm² csa MEB ran in from the house to the garage, linking the steel stanchions and the radiator pipework where it enters the garage.
Does this sound ok?