sprint1

Hi,
Im working on site in worthing and have been asked to find out the length of an installed cable.
Cable size 150mm 4 core
r1+r1=0.3
Ze=0.06
Any help on how to calculate the length of cable would be much appreciated.
 
Find out the resistance of the 150mm cable from the regs.

Example. A ring final cct R1+R2 = 0.55 ohms. It is wired in 2.5 twin and earth

2.5 =7.41 m/ohms/m
1.5 = 12.10 m/ohms/m

7.41 + 12.10 = 19.51

0.55 x 1000 / 19.51 = 28.19 meters.

Hope this helps!
 
roughly the mohms/m (R1+R2) for 150mm Cu is 0.260. so L = (0.3 x 1000)/0.26 = 1154m
 
Last edited:
Ok.
Cable is a 150mm swa/lsf copper conductors.
We were only allowed to do an r1+r1 across the yellow and blue phases as access to the 70mm cpc was unobtainable.i was told that we would be able to determine the cable length from these readings.

Regards Sprint
 
so what you have is the loop resistance of RL2+RL3, both 150mm. so find the value of R1+R2 for 150mm in mohms/m ( i calculated it from the 50mm in table 9A by dividing by 3) then calculate the length.

L= (Rtx1000)/mohms/m
 
Why not use a tape measure?

The cable resistance is dependent on temperature in every part of the cable so using this method could be very inaccurate.
 
Working it out is only an educated guess due to the many variables and its length.
If you cant measure the run then its only method open to you.
Do you need to know the length to work how much beer money is involved:drunk::party:
 
to be honest mate, measuring the resistance is not going to be an accurate way of working out the length of that cable, unless you have a very accurate meter, or you opnly require to find the length tyo withing say 10m on a very long run.

This is due to the fact that on a cable of that size, the resitance is going to be very low, and yopur meter rounding up to the nearest decimal place will have a massive influence on your calculation.
 

Reply to Determining cable length in the Business Related area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I can imagine it just disappearing (loudly) under short circuit conditions, then the resulting blast/plasma etc. casing the busbars to flash over...
Replies
13
Views
705
The repair kit is actually sold by WAGO for that specific purpose (in the wall repair). I had wondered myself about shrinking individually first...
Replies
4
Views
600

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top