Hi there! I have successfully completed all parts of my coursework for level 2 and 3 2365, bar one notorious question:
A trunking run within the electrical switch-room area is to contain the following single-core thermosetting stranded cables
-------------------------------------------------------
Using appendix E of the OSG, I have calculated
35 x 9.6 = 336
25 x 13.9 = 347.5
12 x 18.1 = 217.2
10 x 36.3 = 363
5 x 50.3 = 251.5
336+347.5+217.2+363+251.5= 1515.2
Using Table E5 of the On-Site Guide, and then Table E to identify the dimensions of the trunking using the factor, It is clear that
Trunking factor 1542 is most appropriate, giving a trunking dimension of
100 x 38
---------------------------------------------------------------------
I have been told this is incorrect, and cannot understand where I have gone wrong. I have multiplied the amount of cables by the value of Table E5 (Stranded), added up the total of each cable value, and flicked over to Table E and used the trunking factor equal to or higher than, which is 100 x 38, due to the trunking size being 1515.2
Is there a Spark in shining armour that might add to my knowledge and point me in the right direction. Many Thanks
Ollectrical
A trunking run within the electrical switch-room area is to contain the following single-core thermosetting stranded cables
- 35 x 1.5mm2
- 25 x 2.5mm2
- 12 x 4.0mm2
- 10 x 10.0mm2
- 5 x 16.0mm2
-------------------------------------------------------
Using appendix E of the OSG, I have calculated
35 x 9.6 = 336
25 x 13.9 = 347.5
12 x 18.1 = 217.2
10 x 36.3 = 363
5 x 50.3 = 251.5
336+347.5+217.2+363+251.5= 1515.2
Using Table E5 of the On-Site Guide, and then Table E to identify the dimensions of the trunking using the factor, It is clear that
Trunking factor 1542 is most appropriate, giving a trunking dimension of
100 x 38
---------------------------------------------------------------------
I have been told this is incorrect, and cannot understand where I have gone wrong. I have multiplied the amount of cables by the value of Table E5 (Stranded), added up the total of each cable value, and flicked over to Table E and used the trunking factor equal to or higher than, which is 100 x 38, due to the trunking size being 1515.2
Is there a Spark in shining armour that might add to my knowledge and point me in the right direction. Many Thanks
Ollectrical