A water heater with an output of 5kw is connected to a 230v supply via a bs 60898 type b protective device. the cable is 70 oC PVC insulated thermoplastic coper conductors and the length of cable is 18m. the ambient temperature is 35oC. The cable runs for 300 mm through thermal insualtion. it runs together with one other cable for most of its length and is clipped direct to the wall. Determine the following and show all calcs and refs to tables.
1. Design Current
Ib = 5000/230 = 21.73 A
No diversity according to the on site guide (page 97)
correct
Minimum protective device rateing
In is greater then or equal to Ib = 25 A mcb BS 60898
correct
Correction Factors
It ? = In/caxcgxcixcc
ca=table 6a OSG/ cg = table 6c OSG/ ci = i think table 6b OSG/ cc = 1 i think page 124 OSG ??
correct selection of factors and use of tables
It = 25 / 0.94 x 0.80 x 0.51 x 1 = 65.18 A
correct maths but see below
not sure what do do or say for the
minimum cable rating ??
Minimum cable size
= 10mm2
According to table 6F (osg) and your result you would need 16mm
Maximum allowable voltage drop
= 4.4 according to table 6D on page 130 OSG
Actual Voltage Drop
= (mv/a/m) x ib x l / 1000
= 4.4 x 21.73 x 18 / 1000
= 1.72 A
Volts not amps
is it 5 % of 230 (11.5) so yes that means it doesnt need a bigger cable ?