Hi again ......
I have inherited a central heating system which is oil fired and ancient (mid 1980's), but works perfectly so up until recently I had no reason to go looking for issues.
The only ''new" part is the unvented DHW cylinder which, although it works, has NOT been installed in accordance with the manufacturer instructions.
The current setup is that the manufacturer installed cylinder thermostat and overheat cut-out are not connected at all and never have been (2009 installation date). Instead, the 3-port valve that controls flow through the heating coil is controlled by a pipe thermostat on the hot outlet (recirculating system so this is at cylinder temperature AS LONG AS THE PUMP IS RUNNING - which is why I'm looking at this now, because it's on a timer), and a pipe overheat cut-out, both mounted on the pipe within 150 mm of each other. Both devices are SPDT switches, with 3 core cables
My question - in order to put this system back into compliance, I need to connect the cylinder mounted thermostat and overheat cut-out in place of the existing devices. Problem - the manufacturer fitted devices are SPST devices, which is probably why they weren't used in the first place.
The 3 port in question requires DT switching, as it's positively driven in both directions.
Any suggestions?
I have inherited a central heating system which is oil fired and ancient (mid 1980's), but works perfectly so up until recently I had no reason to go looking for issues.
The only ''new" part is the unvented DHW cylinder which, although it works, has NOT been installed in accordance with the manufacturer instructions.
The current setup is that the manufacturer installed cylinder thermostat and overheat cut-out are not connected at all and never have been (2009 installation date). Instead, the 3-port valve that controls flow through the heating coil is controlled by a pipe thermostat on the hot outlet (recirculating system so this is at cylinder temperature AS LONG AS THE PUMP IS RUNNING - which is why I'm looking at this now, because it's on a timer), and a pipe overheat cut-out, both mounted on the pipe within 150 mm of each other. Both devices are SPDT switches, with 3 core cables
My question - in order to put this system back into compliance, I need to connect the cylinder mounted thermostat and overheat cut-out in place of the existing devices. Problem - the manufacturer fitted devices are SPST devices, which is probably why they weren't used in the first place.
The 3 port in question requires DT switching, as it's positively driven in both directions.
Any suggestions?