...no supp bonding or rcd on lighting circuits in bathrooms. C2 i said. According to esc pdf guide!! Easy fix, spare three ways in 16th ed hager board. Busbar is long enough. Install rcd.

Wondering if i can get any hager one to replace pictured are sizes universal?

I thought save money and get 63a one and mix and match lights and sockets so not all of one on one side etc. 100a a bit generous no??!! Wylex provide 63a seemingly as standard.

Thanks boys and girls ImageUploadedByTapatalk1375822077.561406.jpg
 
The 100A or 63A rating on an RCD is just the maximum current that can safely be put through the device. It does not provide overcurrent protection. Therefore installing a new 100A 30mA RCD would be fine.
 
I know that mate, 100a one is much dearer so was asking can i get 63a (pr thereabouts) one to save money.

Basically, ignore everything else;
ARE HAGER RCDs UNIVERSAL IN PHYSICAL (not CCC or breaking cap.) SIZE?!?!

Fanks!!

Eddie
 
Glad to help mate.
Apparently Hagar are the only manufacturer that maintain specs. so that new breakers can be installed in old boards.
Wish others like Wylex did the same!
How would they make a fortune making us change boards if everything matched there is method in their madness
 
Did you test to see if supplementary bonding was required, at the most no RCD would only be a C3 wouldn't it, as it may not pose a danger even under fault conditions if all other conditions for disconnection times are met !!!! to just slap a C2 regardless doesn't seen right IMO
 
If you have supp bonding but no RCD the ESC guide states C3 however if no supp and no Rcd the its C2. IMO I'd C2 that without testing if supp was necessary,
 
Why not, from advice I've been given by NIC, ESC and other electricians, this would be tested against 17th, whilst ok at time of install(perhaps), it doesn't not comply with current regs, therefore requires some code
 
I Know that but I thought he was looking for a solution to the observation he had made so he could quote to do the remedial work . Just thought it might of been cheaper and easier to do
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Did EICR today...
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
28
Unsolved
--

Advert

Thread statistics

Created
Eddiesparks,
Last reply from
Guitarist,
Replies
28
Views
3,501

Advert

Back
Top