Hi looking for some help about faults and symptoms and difference between short circuit, dead short, and overcurrent to know which fault you have.

Is short circuit line and and neutral fault
dead short zero resistance and a tripped breaker
And overcurrent to much current in circuit causing fires. Any help much appreciated thanks
 
A short circuit is a fault of low or negligible resistance between two conductors which are at different potentials, so it could be a fault between L and N, L and E, L1 and L2 etc.

A dead short is a slang term used to describe the same thing.

Overcurrent means any situation where more current flows than the circuit is intended/designed for, this can be an overload or the current which flows as the result of a fault such as a short circuit.
 
And overcurrent to much current in circuit causing fires.
Fires are started by too much heat (along with a fuel & oxygen of course, but for now think about the heat as the source of ignition).

Too much heat can arise from several causes:
  • Overload - when a circuit is subject to a larger current than the cable(s) are rated for. For example if multiple high current loads are put on sockets fed from the one source. This should not be possible if properly designed as the OCPD (over current protective device - a fuse or breaker normally) ought to disconnect power before the cable will reach a temperature when it can be damaged.
  • Short circuit - basically the same as an overload but a much higher current due to a direct contact between line & neutral (or line-line on 3-phase, etc). Again, this should not cause any damage if properly designed as the OCPD should disconnect very fast such that the let-through energy (referred to as "I2t" but really is current-squared-time) is below the damage threshold of the cable.
  • Bad connection or conductor damage. This has nothing to do with good design as such but is down to poor installation, or the effects of corrosion, or from vibration / thermal cycling causing screw terminals to release slightly, or from a conductor being nicked or strands broken by flexing. Here you get a local hot-spot at the bad connection and almost always gets worse with time.
 
Last edited:

Reply to Difference between dead short and short circuit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
865

Similar threads

Yup will do exactly that when I'm back down there. Thanks for the help
Replies
6
Views
378
Only the N side of the lamp would be at 0v if you went further along the element the voltage would rise.
Replies
14
Views
676

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top