The resistance would need to be a lot higher buddy.Changing a CCU and reconnecting existing wiring (twin and earth) = did a N - CPC IR test for earth leaks prior to dismantling the old (BS3036) unit.
cheers
The resistance would need to be a lot higher buddy.Changing a CCU and reconnecting existing wiring (twin and earth) = did a N - CPC IR test for earth leaks prior to dismantling the old (BS3036) unit.
cheers
The IR might be wonderful but I never mentioned it.
A joint with 0.3Ω resistance, if that is the cause of the odd reading in the neutral, is capable of getting quite hot. E.g. passing 10A it would dissipate 30W and get as hot as a soldering iron. At 32A it would be giving out ten times as much heat. As it's a ring, it would cause more or less incorrect sharing of the total load between the two sides instead, depending on where it's located.
The world is not perfect as you say but it is better to find out the imperfections with the MFT than by tracing the burning smell.
the install is twin and earth.
I see we're thinking along similar lines now. Another theory was that one side of the cable had been 'stretched'. For a bit of mental arithmetic practice, try the following:
A single-core cable of length L1 with resistance 0.41Ω is stretched so that its cross-section reduces uniformly until the resistance is increased to 0.72Ω. What is its new length L2, assuming the resistivity of the copper remains constant*?
* it does change somewhat, when you work metals.
it will not have to be as long
increasing the resistance/metre to an unknown value
What is its new length L2, assuming the resistivity of the copper remains constant*?