Different result every time | on ElectriciansForums
Discuss Different result every time in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Essex
Hi
Has anyone considered that every time you do a continutity/earth loop test, on the same circuit you get a different result every time?
I had an end to end test on a ring circuit today and kept pressing the test button. The results jump all over the place.
How credible is any test if the result is never the same, anyone could make up the results and we wouldnt be able to prove it, and this worries me!
Could be a number of issues, however for a basic continuity i'd say generally an issue with the test kit or operator.
Battery level, instrument accuracy (in cal), lead condition, croc clip connection, pressure of leads on cable ect.. Few of the things i'd initially check
On my tester you need to keep your finger on the test button until it has stabilised. That way I do get the same result each time.
Indeed, good points by Stspark. Always worth remembering that test instruments have an inherent inaccuracy built in - for example it may be +/-10% on some ranges. We shouldn't consider them to be inherently accurate equipment, but more indicative.
Are you waiting between tests , some whack enough current about to warm things
a little , for a different reading next time !
(What gear are you using - does it need its leads zeroing .. (can hide problems!))
Poor connections to meter/leads, do you make sure you null your equipment with the crock clips touching on both their fixed sides?
Is your equipment susceptible to interference? Have you tried isolating other circuits to prove this.
New test kit, calibrated with fresh batteries, constant pressure applied as croc clips secured. Results kept vayring from anywhere between 1.01-1.51 ohms
Send it back for a warranty check ................ if its new kit the results you are getting are unacceptable.
When my Metrel starts doing this, I know its time to replace the leads - which is about every 15 months)
Reply to Different result every time in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Have fitted those before. Not wanting to state the obvious but it is vital that the voltage inputs to the meter, L1, L2, L3 match exactly with the...
Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...