Is it common to get different test results when upgrading a db? Basically I done an EICR in November and came back to upgrade the db and done live tests on all the circuits, but my results were quite different. Like 0.30 ohms out on one circuit
 
Is it common to get different test results when upgrading a db? Basically I done an EICR in November and came back to upgrade the db and done live tests on all the circuits, but my results were quite different. Like 0.30 ohms out on one circuit
please clarify what where you testing at the time .
 
Are your tests after the board change?
Tested before, during initial EICR way last year. Then went back to upgrade DB this week and we live test after upgrading DB, the Zs readings on some circuits were a lot lower than they were. Meter tails were upgraded and the Ze went down by 0.11 but some circuits the Zs was 0.30 lower
 
Tested before, during initial EICR way last year. Then went back to upgrade DB this week and we live test after upgrading DB, the Zs readings on some circuits were a lot lower than they were. Meter tails were upgraded and the Ze went down by 0.11 but some circuits the Zs was 0.30 lower
It might simply be a result of re-terminating all the CPC's properly.
Does it happen to be the case that the ring final circuits are closer to original readings? In theory these will have had the CPC disconnected for fig 8 tests, so should be more recently tightened.
For other circuits it's conceivable that the CPC's weren't touched during the EICR...depending on how the tests were carried out of course.

Then again live Zs tests are notoriously variable and can be affected by electrical 'noise' easily.
 
It might simply be a result of re-terminating all the CPC's properly.
Does it happen to be the case that the ring final circuits are closer to original readings? In theory these will have had the CPC disconnected for fig 8 tests, so should be more recently tightened.
For other circuits it's conceivable that the CPC's weren't touched during the EICR...depending on how the tests were carried out of course.

Then again live Zs tests are notoriously variable and can be affected by electrical 'noise' easily.
Like you say could be a combination of that, and the fact the ze is went down by 0.11 since the tails have been upgraded etc
 
It might simply be a result of re-terminating all the CPC's properly.
My money is on this possibility or something similar. For instance, we have recently had to carry out testing on premises that were dormant/vacant for 2 years (covid related). A number of FLi socket circuit tests were marginally higher than the regs allowed. I did wonder why the installation had been passed in the first place. However as the installation opened up for business again and sockets started to be regularly used we found on retesting some weeks later that Zs values had dropped significantly. Sometimes it can be as simple as a fine film of dust lying on the contacts
 
Of course if you get a high reading on a socket, the usual thing to do is to put the plug (tester plug top) in and out of the socket several times
Yes. That's what would normally be done on getting a high reading. And that's what we did on initial testing, but it did, nt bring the readings down. It was only after several weeks of the sockets been in continuous use that that there was an impact on the readings. I, m just speculating that the long dormant period led to this situation somehow
 

Reply to Different test results after DB change in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
https://professional-electrician.com/technical/replacing-a-consumer-unit-in-a-dwelling-niceic/ All circuits should be tested
Replies
3
Views
1K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
957

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top