To check the stability of a Numeric/Digital differential relay for Generator, 0.8 A was applied from both sides (line side & neutral side) in all 3-phases at opposite direction. Differential current was zero as appeared on relay while restraint current at relay was 1.61A
Can anyone please explain this text to me. Its understandable that why differential current is zero but how restraint current is 1.6 A.
 
Differential protection protects against short circuit faults on geneys, transformers etc.

The current on the ingoing and outgoing sides is monitored on both sides usually by current transformers (C.T's) and this value is what you get at your relay as restraint current.

Now the differential relay monitors this and accepts this as normal hence zero volts on the differential side however, should a short circuit occur and an imbalance be detected then you will have fault current on the differential side of the relay which will be different to the restraint current and cause the protective device to operate.

Also if an external fault travels through the system and becomes an internal fault the relay will pick this up and operate the protective.

This is the best I can offer off the top of my head, hope it makes sense.

Cheers.
 

Reply to Differential Protection in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
275
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
779

Similar threads

Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
993

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top