Went to a house the other day as dining room lights not working. 4 x 40/50w gu10's on a dimmer, dimmer faulty.
Looking round the house there was an incredible amount of incandescent lighting mostly on dimmers so I suggested to customer that it may be worth spending an extra couple of ÂŁ's on the dimmer to get one capable of dimming led lights, they agreed.
Went to cef (the nearest wholesaler) with the faulty dimmer (40-400W rated) and asked for a dimmer that would work on LED's ultimately but on the gu10's now. A couple of phone calls later the guy produced a 60-600W dimmer that he said would be fine. When I questioned him saying that ultimately the load would only probably be 4 x 6W so how would this be suitable he made another call, was put through to a technical department who told him that the dimmer would work with 2 x 7W or 6 x 4W led's and was definitely suitable for led lighting.
Could someone explain the logic of this to me please and how a min 60W rated dimmer would be more suitable than a 40W min rated one. I would have expected something like a 15-200W one!
 
CEF can provide interesting information (using interesting in a variable sense!).
Dimmer design is very much variable and different manufacturers may make a similarly specified dimmer in different ways.
Normally for halogen downlights you would derate the dimmer by at least 25% possibly 50% depending on manufacturer and so you should be looking at about a 400W dimmer for the halogens he has.
Normally for LED dimmers there is no minimum wattage specified only a maximum so if you have a minimum wattage I would be surprised if it worked for anything lower than that minimum.
However it may be that the manufacturer has modified the design of the dimmer but not the labelling!
Possibly the instructions require an additional load resistance in circuit when using low loads?
 
Thanks for the reply.
I did read the instructions before posting (!) and there is absolutely no mention of LED dimming but they assure me that they will work with LEDs however they did specify the minimum loadings / configurations as stated in the original question.
Summarising the statements and specs this unit requiring a min 60W load will work on a 14W load if a minimum of 2 x 7W LEDs are used or a 24W load if a minimum of 6 x 4W LEDs are used.
 
I would tend to set up a test bed and connect up a few LED downlights to the dimmer and see if they dim properly.
Do the instruction state that the dimmer must not be under loaded? If so then you are a bit stuck despite the quality advice from CEF:confused5:.
 
To be fair to the bloke from cef he did make 3 calls to get info and what he reported to me was from the manufacturers technical department. If it was just a counter assistants statement I would have taken it with a very large pinch of salt!
There is nothing in the instructions re loadings, the loading info was on a sticker on the rear of the dimmer.
I am asking mainly out of curiosity's sake. I won't be held to it by the customer as the couple were out and my discussions were with the Romanian mum who couldn't speak English so we were communicating in French (grade C at O level in 1976!!)
 
Hopefully you are going to be OK and maybe someone with better knowledge of dimmer design would be able to provide more information.

Good luck with it, since you have been informed (indirectly) by the manufacturer it is suitable you are following the manufactures instructions!
 

Reply to Dimmer rating not making sense in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
740

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top