Hi guys,
Recently installed a 12kW electric shower for a customer.
Customer has called me back because the lights dim quite noticeably every time he uses it.
Took some readings at the CU Main switch. Shower off = 248V, shower on = 236V, a voltage drop of around 12V (although still in tolerances 230V +6/-10%). This drop seems quite high, as I've installed the same shower in other properties and not seen any noticeable voltage drop or lights dimming (although I know 10m is quite a long run).
Ze at the service cut-out fuse is 0.15ohms, TN-S.
Incoming is 100A BS88. Meter tails are 25mm.
Cable size is 10mm, length of run is 10m, no grouping, clipped direct, no insulation.
Circuit is on 80A RCD / 50A MCB with no other siginificant circuits. No other significant power users whilst testing - just shower & lights. Lights are on the other RCD.
R1+R2 between CU & shower is 0.11ohms.
There is a 50A isolation switch about 2m from the shower. Current reading when shower is in use is about 55Amps (which seems about right). According to my calcs, 10mm @ 10m should result in voltage drop of no more than about 2.5V.
(ps, I know that 50A MCB + isolation switch is less than 55A looad, but using the 1.45x / hour rule and the NICEIC diversity/heating circular regarding average length of shower v heating effects - anyway, MK don't make a 63A MCB or a 63A isolation switch as far as I'm aware - just before everyone jumps on their hobby-horse about this)...
Anyone got any ideas why there should be such a large voltage drop (customer is worried about his dimming lights)?
Some threads seem to think it may be a DNO transformer on the way out, others that there might be a high resistance problem with the isolation switch (which I'm going to swap out anyway, just in case).
Thanks
Sparkie Stu
NICEIC Registered Domestic Installer
Recently installed a 12kW electric shower for a customer.
Customer has called me back because the lights dim quite noticeably every time he uses it.
Took some readings at the CU Main switch. Shower off = 248V, shower on = 236V, a voltage drop of around 12V (although still in tolerances 230V +6/-10%). This drop seems quite high, as I've installed the same shower in other properties and not seen any noticeable voltage drop or lights dimming (although I know 10m is quite a long run).
Ze at the service cut-out fuse is 0.15ohms, TN-S.
Incoming is 100A BS88. Meter tails are 25mm.
Cable size is 10mm, length of run is 10m, no grouping, clipped direct, no insulation.
Circuit is on 80A RCD / 50A MCB with no other siginificant circuits. No other significant power users whilst testing - just shower & lights. Lights are on the other RCD.
R1+R2 between CU & shower is 0.11ohms.
There is a 50A isolation switch about 2m from the shower. Current reading when shower is in use is about 55Amps (which seems about right). According to my calcs, 10mm @ 10m should result in voltage drop of no more than about 2.5V.
(ps, I know that 50A MCB + isolation switch is less than 55A looad, but using the 1.45x / hour rule and the NICEIC diversity/heating circular regarding average length of shower v heating effects - anyway, MK don't make a 63A MCB or a 63A isolation switch as far as I'm aware - just before everyone jumps on their hobby-horse about this)...
Anyone got any ideas why there should be such a large voltage drop (customer is worried about his dimming lights)?
Some threads seem to think it may be a DNO transformer on the way out, others that there might be a high resistance problem with the isolation switch (which I'm going to swap out anyway, just in case).
Thanks