J

James Sutton

Hello All

Have just ran a new 6mm SWA cable 230v single phase supplying an iverter ACU from a 4th floor dis board to the roof. I am unable to isolate the dis board as it servers computer room power racks so i cannot do a Ze test as i cannot disconect the main earth. Also how do i carry out a ZS at the board i no i need the power on to carry out a Zs/PFC at the dis board but i cannot turn off any outgoing MCBs to other ccts

should i just carry out the ZS/PFC at the board with MCBs to other ccts on. i know i have to carry out ZS at points on my installation. But i think on the schedule of test results it asks for Ze ZS and PFC at the orgin.

They have also used a 24way merlin gerin 3phase board but only taken a single phase supply from the rising busbar what came as abit of a shock when looking at the board as the main switch is a 4pole 125A. but all MCBs on all phase have power but on the switch there only using L1 and there also switching the neutral

Any thoughts please. Nothing has goner right on this job glad when its done should be monday will try and upload some photos

Thanks
James Sutton
 
If it is not possible to carry out Ze and PSC you should note on the cert the reasons......can you not arrange to test out of hours?
No reason why you cant carry out Zs and PSC tests at the DB with final circuits energised,as long as there are no RCD's on the distribution circuit.
The TPN DB will have the 3 phase connections linked....nothing wrong with that as long as the DB is labelled as single phase.
 
Are the servers not on ups? In a fActory I'm working In, I'm allowed 10 mins too isolate the installation before the ups runs out of juice
 
There are no RCDs on the dis board. So carrying out an Zs on the board should be ok then? Cant do out of hours either IT wont let us shut the board down as it causes them to much work.
 
so, if there,s a power cut, do they all run round like headless chickens screaming" my pc's gone down, i can't get on facebook. jeezus i'll have to speak to the guy at the next desk instead of sending an email" ?
 

Reply to Dis board nightmare in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
834

Similar threads

  • Question
Had this before, found by the DNO to be a corroded fuse carrier on a pole mounted fuse on their LV network
Replies
1
Views
716
  • Question
"A catalogue of errors" would be the appropriate phrase here and I agree with Avo and James that HSE need to be involved rather than this forum...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top