Any 1 no where i can get to c talbes for lightin circuits,concerning mcbs to ctrl various circuits.Designers for 6x250 watt low bay ,told that these will be ok on a 10 amp c type breaker,their total is 6 amps,jus a bit wary of that really,my idea 6x1.8=11amps which then puts the mcb up to 16 amps wots your views on this.We recently done a designed low bay circuit,4x400 watt these were backed by a 25 amp c type breaker b intersesting 2 c your opinions ta ra bab
 
calculate your cable size (1.5mm?) according to load then calculate the volt drop . depending on length of run you may have to up to 2.5mm . then size your MCB accordingly.
 

Reply to Discharge lightin in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
307
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
830
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
929

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top