C
Chappers
Hi everyone, I was with Chief Big Spark at work doing some periodic inspection and testing on units. Chief was doing the testing, I was giving him emotional support cos were using his meter and he doesn't like others looking at it or tocuhing it. Very possessive, poor thing. He says he has always tested RCDs with appliances in the location still connected, but on that day he did the RCD test and found it wasn't tripping off in <40ms. In fact it was 120ms. Changed the RCD and result was the same. Changed it again, still same. Never happened before, he said, so was confused. While he was planning to strip the place down, I came up with the idea that something plugged in may be altering the reading, and was right - when the fridge compressor was running, the RCD was, according to the meter, knocking off in 120ms. With the fridge disconnected or compressor not running, it was 26ms.
Does anyone else ensure everything is unplugged/disconnected, and does anyone know why it was altering the tripping time of the RCD. Or maybe the RCD was tripping off more quickly, but meter reading was being affected somehow by fridge...
Ta.
Does anyone else ensure everything is unplugged/disconnected, and does anyone know why it was altering the tripping time of the RCD. Or maybe the RCD was tripping off more quickly, but meter reading was being affected somehow by fridge...
Ta.