They are logarithmic graphs, that's why the scales are non-linear.
From left to right, starting at 1, the increments are 1 up to 10, then increments of 10 up to 100, then increments of 100 up to 1000, etc etc ...
For 418A, call it 400A, look at the 3rd line after 100, that's 400A.
Then look where the curve cuts that line, then the value on the time axis is your disconnection time.
BUT, a 32A curve is all to the left of the 400A line, so take the lowest time on the 32A curve as your disconnection time, that is 0.1sec
Hope that helps, but it's possibly confused you even more.
Blame my chronic explanation!!!