I know it’s good practice to disconnect the functional earth when doing an insulation resistance test but my assessor has told me that he thinks you should disconnect the functional earth when you measure Zs?
Which I don’t understand does anyone else do this? And is he correct?
 
Yeah sorry forgot to mention that, I’m just wondering about disconnecting the functional earth when measuring Zs
 
Not sure the functional earth would have an impact. Might be worth doing 2 test, 1 with it connected and one with it disconnected.

I'd be interested to know the difference in results
 
I have never known that to be advised before.
Some manufacturer’s advise disconnecting L & N as well as both the Neutral and FE flying leads, before conducting an IR test.
 
Very interesting I’ll check and see if it makes a difference and let you know :) well my assessor also told me you could measure Zs at the distribution board! Which is insane that’s why I thought I would check with you guys :)
 
No.
Ze would be measured at the DB/CU by disconnecting the Installation Earth conductor from the MET.
Zdb would be measured at the DB/CU with the Installation Earth conductor, bonding conductors and CPCs connected.
 
You might get the same reading.
I would expect it to be slightly to quite a lot lower depending on the type of earthing.
Don’t know that it proves anything, other than there may be parallel earths.
 
Ze is a measurement with just the suppliers earthing conductor performed at the main incoming point (usually the first DB, C/U)

Zs is a measurement usually at the end of a circuit, fitting, accessory to confirm compliance with Zs values.

Zdb is performed at a sub board. This will measure the earth path prior to the board your measuring at. This could be through numerous other boards.

I think that's right? :-/
 

Reply to Disconnecting the functional earth on an rcbo in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
864

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top