This might help a few of us suffering the 2391 exam.
Maximum disconnection times for a nominal rms line voltage to earth, U0 of 230V
Firstly for a TN system:
Final circuits not exceeding 32A = 0.4s
Final circuits exceeding 32A = 5s
Distribution circuits = 5s
For a TT system
Final circuits not exceeding 32A 0.2s
Final circuits exceeding 32A = 1s
Distribution circuits = 1s
A maximum disconnection time of 5s applies to all circuits in a reduced low voltage system.
A maximum disconnection time of 5s applies to all circuits supplying fixed equipment used in highway power supplies.
I'm still not sure about electrically separated circuits.
I mean if we have a 50V SELV circuit and we get a line to neutral fault on the low voltage side does this mean the disconnection time is 5s?
Seems a bit long to me.
There seems to be a lack of clear guidance when testing electrically separate circuits for insulation resistance and disconnection times.
Anyway, hope this table helps.
Just one more question.
What is the logic behind a five second disconnection time.
Why is it some circuits are allowed a five second disconnection time and others not?
Maximum disconnection times for a nominal rms line voltage to earth, U0 of 230V
Firstly for a TN system:
Final circuits not exceeding 32A = 0.4s
Final circuits exceeding 32A = 5s
Distribution circuits = 5s
For a TT system
Final circuits not exceeding 32A 0.2s
Final circuits exceeding 32A = 1s
Distribution circuits = 1s
A maximum disconnection time of 5s applies to all circuits in a reduced low voltage system.
A maximum disconnection time of 5s applies to all circuits supplying fixed equipment used in highway power supplies.
I'm still not sure about electrically separated circuits.
I mean if we have a 50V SELV circuit and we get a line to neutral fault on the low voltage side does this mean the disconnection time is 5s?
Seems a bit long to me.
There seems to be a lack of clear guidance when testing electrically separate circuits for insulation resistance and disconnection times.
Anyway, hope this table helps.
Just one more question.
What is the logic behind a five second disconnection time.
Why is it some circuits are allowed a five second disconnection time and others not?