Ok lets not get bogged down with this, maybe i am thinking about it too deeply.
If i have a distribution circuit then the disconnection time is five seconds. Are the circuits supplied from this distribution circuit then classed as a final circuits and then subject to the 0.4 second disconnection time provided they are protected by a device of 32 amps or less.
 
Right well I'm having arguments at work with a fellow' tester'Basically its an old installation 40+ all bs88 fuses, its a tn system so 32 and under should be 0.4 is my view however he argues there all 5s because a bs88 fuse cannot achieve a 0.4 disconnection time without the installation being protected by a trip, can't find much in the regs because the install is so old
 
Last edited:
Right well I'm having arguments at work with a fellow' tester'Basically its an old installation 40+ all bs88 fuses, its a tn system so 32 and under should be 0.4 is my view however he argues there all 5s because a bs88 fuse cannot achieve a 0.4 disconnection time without the installation being protected by a trip, can't find much in the regs because the install is so old

Of course they can achieve 0.4s if the fault current is high enough. Have a look at Table 41.2 BRB for Max Zs values for 0.4s.

Basically...

TN system

Final circuits ≤ 32A = 0.4 seconds
Final circuits > 32A and distribution circuits = 5 seconds

TT system

Final circuits ≤ 32A = 0.2 seconds
Final circuits > 32A and distribution circuits = 1 second
 
Right well I'm having arguments at work with a fellow' tester'Basically its an old installation 40+ all bs88 fuses, its a tn system so 32 and under should be 0.4 is my view however he argues there all 5s because a bs88 fuse cannot achieve a 0.4 disconnection time without the installation being protected by a trip, can't find much in the regs because the install is so old

As fellow 'testers' I'm a bit concerned that neither of you could access the facts without the help of a forum?

It's pretty basic stuff....
 
Yes well my copy of bs7671 wasn't available to show him the regs, iv only got into testing full time recently and the other tester has been doing it for 30+ years and wouldn't belive me. I have quite a few doubts about him but hes been the main/only tester the company I work has ever had and does not take kindly to me questioning him. But thanks for you knowlegable responses
 

Reply to Disconnection times in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Yes Table 3A that was in Appendix 3 of the 17th edition of BS7671 and in BS 7671:2018 (Blue Book) up to the release of BS7671:2018 +A2:2022 (Brown...
Replies
11
Views
556
On the minor works in the brown book it has Zdb
Replies
3
Views
309

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top