Circuits under 32A the disconntion times would be 0.4 and anything over woud be 5 am i right.
 
Not sure what you mean but TT disconnection times are either 0.2 secs or 1 sec.

5 sec disconnection time is for sub mains and circuits over 32A for TN systems

Correct, the op was Circuits under 32A the disconntion times would be 0.4 and anything over woud be 5 am i right. Unless your working on a TT system
 
Correct, the op was Circuits under 32A the disconntion times would be 0.4 and anything over woud be 5 am i right. Unless your working on a TT system
Not quite.
With a TN system, the 0.4s disconnection time applies to final circuits upto and including 32A. (Lights, boilers, RFCs, etc.)
The 5s disconnection time applies to final circuits over 32A and any distribution circuits. (Cookers, showers garage/shed supplies, etc.)
In some very rare cases, the same disconnection times are allowed for TT systems.
However in general, the disconnection times are reduced to 0.2s and 1s respectively.
 
Yeah, i should have put a bit more detail into my original post. I can see the disconnection times in my BRB.
I was just getting confused with the definition of a distribution and final circuit. Could not decide wether or not circuits supplied from a distribution circuit were classed as final circuits
 

Reply to disconnection times in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
814
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
873

Similar threads

On the minor works in the brown book it has Zdb
Replies
3
Views
297
Yes, probably overthinkig, thanks.
Replies
6
Views
600

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top