Hi. I'm currently doing my design project and have submitted the first draught I've managed to correct most of my feedback but am struggling with question 5, Determine, for one of the fridges the minimum possible CSA area of CPC which will satisfy the requirements disconnection as ads under earth fault conditions and the adiabatic equation as reg 543.1.3. The feedback I received for my first attempt was suggestive of thermal constraints and that it talks about ADS remember it's 16A *5 80A. How do I go about this as I always seem to go back to my original answer? Thanks
 
Hi. I'm currently doing my design project and have submitted the first draught I've managed to correct most of my feedback but am struggling with question 5, Determine, for one of the fridges the minimum possible CSA area of CPC which will satisfy the requirements disconnection as ads under earth fault conditions and the adiabatic equation as reg 543.1.3. The feedback I received for my first attempt was suggestive of thermal constraints and that it talks about ADS remember it's 16A *5 80A. How do I go about this as I always seem to go back to my original answer? Thanks
This is telling you to run the adiabatic equation in Part 5 (Selecting conductor CSA - S = √(I2t)/ k) and not the one from Part 4 (Thermal Withstand - t = k2s2 / I2). You can run thr part 4 equation but you'll already know what disconnection times you'll need to hit.

If your sizes work out then the last check is I2t < K2S2 - Is thr energy let through WITHIN (or less than) the total energy that thr conductor will take before degrading.

Don't forget to add statements to the fact at each part of the equation;

"I believe % under reg # is met because" (or the inverse; is NOT met because)

For % substitute the part of the process; coordination, volt drop, thermal withstand, conductor sizing etc)

For # substitute the regulation number that applies.

Where you're saying the design is not compliant then you need to offer resolutions (bigger cable/OCPD), bonus points for mentioning consideration for Appendix 17 and consideration of potential saving in energy efficiency vs outlay
 

Reply to Disconnection under ADS in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Spot on The Requirements of sections 1-6 must be complied with in a special location unless its otherwise stated in that part of section 7 that a...
Replies
4
Views
78
  • Question
After fitting out the first room of downlights.... i expect him to get a bit speedier at fitting them There is so many unknowns to price at this...
2
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top