Does anyone know or where to find the calculation you do to find a fault/break in a circuit that can't be physically traced.I'm sure i've seen it somewhere in one of my books but can't remember.

Cheers
 
If its a break then to find the fault you need a TDR (Time domain reflectometer), it basically sends a signal down the wire and at the break the signal gets 'reflected' back, based on the time it takes the signal to return, it can tell you how far down the cable the fault is.

If the fault is a dead short between cores then by doing a resistance measurement between the shorted cores and knowing the resistance of the conductor (based on CSA) per meter, you maybe able to gauge how far away the 'short' is. If the 'short' is not a 0 ohm short then you've got a problem!
 
If it is a dead short say on a radial caused by a nail connecting two of the conductors(if it is a ring disconnect one end) test resistance between conductors at CU and sockets - the position with the smallest reading is the closest. Identify the conductor size - and look up the resistance per metre in table 9A of the OSG for the size of the conductors involved. Divide that value into the lowest resistance reading and you have the distance of that reading from the fault.

Only works really well if you have a very good contact between conductors, but even if it is not perfect can still get you close to it.
 

Reply to Distance Calculation to find fault in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
829

Similar threads

  • Question
A lot will depend on the load on the tray / basket / trunking and the span before it bends / distorts
Replies
2
Views
537
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top